(62) NFPA 96, 2004 Edition, Standard for Ventilation Control and Fire Protection of
Commercial Cooking Operations
Modifications:
(a) Modification to Chapter 1:
1. Delete subsection 1.1.3 in its entirety and substitute in its place the following:
“1.1.3 This standard shall apply to all commercial cooking equipment used for
commercial cooking operations.”
2. Delete subsection 1.1.4 in its entirety and substitute in its place the following:
“1.1.4 This standard shall not apply to residential cooking equipment located in a single
dwelling unit or to cooking equipment in facilities where all of the following are met:
(1) Only residential cooking equipment such as stoves, ranges or cooking surfaces
traditionally used in dwelling units are being utilized.
(2) The defined residential cooking equipment contains a maximum of four standard
surface cooking elements and is not used for frying operations.
(3) The defined residential equipment is used for food warming, limited cooking,
rehabilitation training or in a home economic education classroom setup.
(4) The residential cooking equipment is protected by a listed self-contained residential
fire suppression system located in an approved residential hood which is vented directly
to the outside and providing protection to each cooking surface
Exception to (4): The self-contained fire suppression system for the defined residential
cooking equipment need not be provided where protection is provided by an approved
automatic sprinkler system protecting the cooking surface, subject to approval of the
authority having jurisdiction. Required use of automatic disconnects of the fuel source or
power source is subject to approval of the authority having jurisdiction.
(5) The facility is not an assembly occupancy.
Exception to (5) Church facilities with a single residential stove or range complying
with (2) above.”
(6) Fire Extinguishers are located in all kitchen areas in accordance with NFPA 10,
Standard for Portable Fire Extinguishers.
“3. Add a new subsection 1.1.5 to read as follows:
“1.1.5 This standard shall not apply for conditions existing prior to the effective date of
this standard subject to the authority having jurisdiction where a notarized statement that
no frying operations will be preformed is provided.”
(b) Modification to Chapter 10:
1. Delete subsection 10.2.3 in its entirety and substitute in its place the following:
“10.2.3 Automatic fire extinguishing systems shall comply with UL 300, Standard for
Fire Testing of Fire Extinguishing Systems for Protection of Restaurant Cooking Areas,
or other equivalent standards and shall be installed in accordance with the requirements
of the manufacturer’s installation and maintenance manual.
“Exception No. 1: Systems (dry or wet chemical) installed prior to 1998, and which are
in compliance with the manufacturer’s listing. These systems shall be red tagged as non-
UL 300 compliant and must be replaced to a UL 300 compliant system when any of the
following apply:
“a. Appliance arrangement has been modified, or the hazard has been modified to
create a higher risk since the initial system installation.
“b. The system is discharged.
“c. The system is due for 6-year maintenance or is due hydro-testing.
“d. If listed manufacturer’s replacement parts, or the required extinguishing agent, are
needed but are not available.”
2. Delete subsection 10.2.6 in its entirety and substitute in its place the following:
“10.2.6 Automatic fire extinguishing systems shall be installed by competent personnel
meeting Chapter 120-3-23, Rules and Regulations of the Safety Fire Commissioner,
licensing and permit requirements, in accordance with the manufacturer’s instructions,
and the following applicable standard(s):
“(1) NFPA 12, Standard on Carbon Dioxide Extinguishing Systems
“(2) NFPA 13, Standard for the Installation of Sprinkler Systems
“(3) NFPA 17, Standard for Dry Chemical Extinguishing Systems
“(4) NFPA 17A, Standard for Wet Chemical Extinguishing Systems”
3. Delete paragraph 10.10.1 in its entirety and substitute in its place the following:
“10.10.1* Portable fire extinguishers shall be installed in kitchen cooking areas in
accordance with 4.3.2 of NFPA 10 and shall be specifically listed for such use. An
approved type portable fire extinguisher and a placard as required by 4.3.2.2 of NFPA 10
shall be installed within 5 feet of each means of manual activation for the exhaust hood
fire-suppression system.”
4. Delete Section 13.2 in its entirety and substitute in its place the following:
“13.2 Design Restrictions. All recirculating systems shall comply with the
requirements of Section 13.2. Recirculating systems shall be limited to outdoor vending
areas or rooms that are fully sprinklered.”