1 The system looks to be a Pyro Chem, not Ansul. The plenum nozzle is mounted OK
2. the link holder is upside down. It is upside down because they mounted in too low in the plenum, they wanted the link holder to match the contour of the sheet metal
3. The link holder is out of the air stream, the activation of the system will be delayed.
4. The link holder at the duct entrance will be a bithch to service.
5. I have put sytems in some Gaylord hoods, the last 2 were in hospitals. I had the water wash deactivated during the fire suppression activation.
6. If the water wash is active, the chemical will cause rapid deteriation of the corner pulleys. This will cause the system to not activate. Only Amerex has a mechnical detection system that does not use corner pulleys.
7. Arn't Gaylord Hoods a pain to clean? One of our accounts has a Gaylord water Wash over a charbroiler. The first time we cleaned the hood, every time my helper carried stuff up the 2nd floor kitchen, he put chemical on it. Every time I carried stuff up the the 2nd floor kitchen, I put chemcal on it. Neither of use knew the other was squiting chemical in the hood. After plugging up the drain as least 3 times, we figured the hood was clean. We did the tear-down, polished the Stainless, and were ready to leave. I stuck my hand up the hood and pulled down a glob of grease the size of my fist. It took 3 years before I was pleased w/the job. Last year I got them to let me service the Gaylord water wash. There are 7 hoods w/water wash. $3693.75
later, a bunch of nozzles(some replaced 3 times) and now the water wash hoods actually work, somewhat. More or less, as well as a water wash will ever work