Boston Fatal fire last month

Grant

Administrator
Tougher standards are on the table when it comes to getting rid of grease in Boston restaurants after two Boston firefighters died in a West Roxbury restaurant fire last month.

NewsCenter 5's Steve Lacy reported that there is currently no certification process in Boston for companies involved in grease cleaning. Critics have argued that has led to an unregulated industry that is open to just about anyone, regardless of whether they have the training required to do the job properly.

A preliminary investigation indicated that it was a grease buildup in a kitchen exhaust pipe that caused the fire that killed two Boston firefighters, Warren Payne and Paul Cahill, at the Tai Ho restaurant on Centre Street last month. The fire occurred despite the fact that the restuarant had its vents cleaned just two months earlier.

In response, the Boston Globe reported that members of the Boston City Council are now preparing to draft legislation requiring new certification requirements for companies hired by restaurants to remove grease.

The push for more oversite, which is said to have the support of a majority of the council, would establish training requirements for all grease-removal workers. Lawmakers at the Statehouse are also planning to draft similar legislation that would apply to cleaning companies statewide.

More changes will likely be made to city and state fire codes after the investigation into the deadly fire is completed, but the final report is not expected until next year.
 
It's a real shame that it takes a tragedy of that magnitude to get people off their @sses and weed out the hacks.
 
Tgp

Sic The Grease Police on 'em. I'm sure the coppers know an opportunity has arisen to present the people and their representatives with a viable, and reasonable certification scheme.

If you think certification/regulation is the answer, the time is now. Massachusetts has seen entirely too many firefighter deaths since the eight brave men that died in that Worcester warehouse fire around 2000. Maybe they can be swayed.

Are you ready greasers?
 
Why was the system never inspected by the local AHJ? Change will only come when the AHJ's becomes accoutable and the cleaners condition report are sent to the AHJ for review and action. Inspections only come after the red trucks are polished.
 
The actual invoice from the exhaust cleaner showed hood and fan cleaning and did not include duct cleaning.
 
The West Roxbury restaurant where two firefighters died Wednesday in a blaze fueled by built-up grease in the ceiling had a history of code violations for greasy equipment and vents and was eight months overdue for a health inspection that would have included a review of the ventilation system.

City records show that health inspectors last visited Tai Ho Mandarin and Cantonese Restaurant in June 2006, when it was cited for minor violations, but received a passing grade. A year earlier, health inspectors cited the restaurant for excessive grease on the fume hood and other kitchen equipment. Under state regulations, the restaurant should have been inspected every six months, but the city failed to conduct the last two required reviews.

Thomas J. Goodfellow, director of the Inspectional Services Department's Division of Health Inspections, refused to say why city inspectors had not been to the restaurant for more than a year, but acknowledged that the restaurant was overdue for an inspection.

Health inspectors are not charged with detecting fire hazards, but do inspect kitchen equipment and ventilation for grease buildup. The question of whether regular inspections would have detected the problem received varying responses from City Hall.

Goodfellow said he did not know whether an inspection of Tai Ho would have caught the grease buildup. "Inspectors can't see the pipe above the hooded area," he said. When it was last inspected, some 14 months ago, he said, "no grease had leaked down."

Dorothy Joyce, a spokeswoman for Mayor Thomas M. Menino, said there is no connection between the irregular health inspections and the undetected fire hazard at the restaurant.

Fire officials said yesterday that a preliminary investigation indicated that grease that had seeped over time from the ventilation system into a 10-inch crawl space ignited and burned undetected in the ceiling for more than an hour. Fire officials said it is still unclear what provided the spark. When the firefighters of Engine 30 and Ladder 25 arrived for what they believed was a routine kitchen fire, the ceiling suddenly collapsed and they became trapped in the deadliest blaze for Boston firefighters in 26 years. Two firefighters were killed, and 10 more were treated for injuries and released.

As the city yesterday mourned the deaths of Warren J. Payne, 53, a 19-year veteran, and Paul J. Cahill, 55, a 14-year veteran, the Boston Fire Department launched an investigation into the fatal fire. Veteran fire officials said they were stunned by how quickly the blaze forced firefighters to shift from extinguishing the fire to get to their dead and wounded. Only 11 minutes elapsed between the first 911 call and the moment a firefighter caught in the blaze hit the panic button on his radio.

"They ran a hose line into the building, thinking to themselves `This one is going to be easy,"' Fire Chief Kevin P. MacCurtain said. "When they started to extinguish the fire, something unexpected happened, something that we haven't seen at this type of fire."

Mourners yesterday piled flowers outside the Engine 30 and Ladder 25 station house on Centre Street, five blocks from the charred restaurant. Governor Deval Patrick ordered flags to half-staff. Fans observed a moment of silence during the Red Sox-Yankees game in the Bronx.

"We are all aware of the risks our public safety officers take to protect us," Menino said. "They always put our needs before their own. That doesn't make it any easier to accept the harsh reality we find ourselves in today."

As donations poured into funds for the firefighters' families, problems with the restaurant's maintenance came to light. Under state regulations, the city is required to conduct health inspections at restaurants every six months. In addition to food safety issues, city health inspectors are supposed to check the hoods over cooking equipment for buildup and the filters between the hoods and the pipes that take greasy exhaust up to the roof.

"If the inspector notices that they're dirty or that there's an accumulation of grease on there, they will be cited," said Goodfellow.

The Fire Department also conducts its own random checks at restaurants and in response to complaints, but is not required to regularly conduct inspections.

Steve MacDonald, a Fire Department spokesman, said fire inspectors have cited the restaurant five times since 2001. In April 2001 and March 2005, the restaurant was cited for not cleaning the hoods over the stoves and the ceiling ducts, which drew grease and hot gas from the kitchen to the roof outside. MacDonald said the restaurant fixed the problems after being cited, and the Fire Department was satisfied.

When city health inspectors went to the restaurant in September 2005, they found a series of health code violations, including excessive grease on the kitchen hood, lights, vents, and pipes. The inspector ordered the restaurant to clean the equipment, but records show that the inspector never verified that the violation was corrected. The city's own rules require that the inspector check to make sure the violation is corrected at the next visit, but there is no record of this in the 2006 inspection.

The restaurant was next inspected in June 2006, when health inspectors found more violations, including greasy cardboard boxes being used for storage. The staff removed the boxes during the inspection, and the restaurant received a passing, but not exemplary, grade.

A woman who answered the phone listed for Tai Ho's owner hung up on a reporter seeking comment yesterday. The building's owner, John C. Kennedy Jr. of Newton, also declined to comment.

In Boston, the number of restaurant inspectors has been cut from 22 to 18 in the last five years. According to federal guidelines, the city should have between 28 and 30 inspectors. The inspectors are responsible for overseeing 4,799 licensed establishments that serve food.

Menino, citing budget constraints, has said in the past that he cannot afford to restore the four positions that were cut, much less hire 10 or 12 inspectors.

Fire officials believe the mix of flames and toxic gases trapped in the ceiling intensified when a massive air conditioner fell through the roof and into the ceiling, providing fresh oxygen for the flames. At the same time, firefighters may have poked at the ceiling from below to ventilate the fire, fire officials said. A fire ball erupted, engulfing Payne. Cahill died in the smoke and heat.

Payne was among the first firefighters to rush inside the restaurant. He searched for patrons and employees, unaware they had all fled. Cahill was right behind him, holding the nozzle of the fire hose and spraying water at the kitchen ceiling. Suddenly, the ceiling collapsed, unleashing the fireball. A firefighter hit the panic button on his radio. When emergency workers outside radioed back, they received no response.
 
J&B Cleaning had a three-month contract to clean the hood cover, fans on the roof, stove area and the floor under the stove at the Tai Ho Restaurant. A J&B spokesperson said that the company last cleaned up at the 1727 Centre St. restaurant on June 21 and was slated to return again on Sept. 21.
 
Fire's fuel apparently missed
Receipt indicates exhaust pipe not cleared of grease

By Donovan Slack, Globe Staff | September 7, 2007

The owner of Tai Ho Mandarin and Cantonese Restaurant has given city officials a receipt indicating that a company hired to remove kitchen grease at the West Roxbury eatery in June did not clean the kitchen exhaust pipe. Firefighters have said grease buildup in that pipe fueled a blaze last week that killed two Boston firefighters.

The receipt from Roslindale-based J&B Cleaning says its staff worked in the kitchen below and climbed onto the roof above to clean an exhaust fan. But it does not say they cleaned the crucial area in between - where fire officials say the hidden grease was leaking.

There is no indication on the June 21 receipt that the cleaners even examined the vent for grease buildup.

State fire codes mandate quarterly inspections of entire kitchen exhaust systems and the cleaning of any buildup found. The codes charge restaurant owners with the ultimate responsibility for making sure it is done right.

Fire Chief Kevin MacCurtain has said grease from the exhaust pipe oozed into a crawl space above a ceiling, where it ignited Aug. 29 and burned undetected for at least an hour before firefighters arrived.

Industry specialists say a thorough inspection and cleaning two months before the fire would have revealed any buildup or leaks. They say the cleaning receipt points to an industrywide problem: National standards for the inspection and the cleaning of restaurant grease are weak, and state and local regulation of grease-cleaning companies in Massachusetts is virtually nonexistent. As a result, many companies inspect and clean grease only from visible areas - stoves, exhaust hoods, and walls, for example.

"This is, for the most part, a one-or-two-men-and-a-dog-and-a-truck kind of business," said Steven Schlesinger, co-owner of Tri State Fire Protection and Tri State Hood & Duct, which cleans restaurants in Maine, New Hampshire, and Massachusetts, including large chains such as Burger King. "There are people with a boom box and a pressure washer who go out there and say they're hood-cleaning specialists. But it's not as simple as that."

A man who answered the phone at J&B Cleaning declined to comment, and the company owner, Joy Bell Tsui, did not return a message left with his son at the Claxton Street residence where the company is headquartered.

A woman who answered the phone listed for the president of the company that owns Tai Ho, Qi Chun Li, hung up on a reporter seeking comment yesterday.

National fire codes, which Massachusetts adopted several years ago as state codes with the force of law, require that kitchen exhaust ducts "be inspected for grease buildup by a properly trained, qualified, and certified company or person(s)." But the code leaves it to state and local fire officials to decide what qualifications, training, or certifications are necessary in each jurisdiction.

In Massachusetts, there are no training, certification, or licensing requirements for grease-cleaning companies. State fire codes give authority over instituting such requirements to local fire departments. In Boston, no such requirements exist.

Boston fire officials declined to say why yesterday. "We're going to let the investigation run its course before saying anything," said Steve MacDonald, department spokesman.

The receipt for the Tai Ho cleaning, which cost $500, was provided to city officials by the owner of the restaurant, and the city provided it to the media.

The Globe reported last week that city health inspectors had not visited the restaurant for more than a year, even though state regulations require the city to inspect restaurants twice a year. Just after the fire, city officials rebutted allegations that there was any connection between the missed inspections and the grease buildup that fueled the fire.

Grease-cleaning specialists say most restaurants entrust inspections and cleaning to a single company. Typically, workers begin with a visual inspection of duct work, inside and outside. To detect leaks, they use a flashlight to look for grease accumulation at seams in the ducts.

If part of the duct is inaccessible or concealed within a crawl space, as may have been the case at Tai Ho, the workers are required to note that on their cleaning and inspection report, according to Scheslinger and fire prevention engineers at the National Fire Prevention Association, which issues the national codes adopted by Massachusetts.

It's unclear whether the owner of Tai Ho maintained any inspection reports. It also is unclear whether the owner entrusted quarterly inspection as well as cleaning duties to J&B Cleaning. Based on statements from fire officials about the cause of the blaze, specialists said, grease should have been detected.

"If there was enough up there to burn for an hour, you would have seen some accumulation on the duct," said Kathy A. Notarianni, head of the Department of Fire Protection Engineering at Worcester Polytechnic Institute.

At Tai Ho, however, there were two ceilings below the crawl space, and fire officials have said the grease buildup was in the upper layer. Specialists said the double-ceiling construction may have hidden the telltale ceiling stain that signals grease buildup.

Double-ceiling construction is not uncommon in Massachusetts, Notarianni said. "It creates a concealed space so the fire is allowed to burn undetected," she said.

There were 280 restaurant fires in Massachusetts in 2005, the last year for which figures are available. They collectively caused 10 firefighter injuries, three civilian injuries, and $5 million in damages, according to the state Department of Fire Services.

Sixty percent of the fires started in the kitchen, with 5 percent, or 14 fires, starting in chimneys or grease-exhaust pipes.

Across the nation, firefighters responded to 8,520 fires in bars and restaurants between 2000 and 2004, according to the National Fire Protection Association. The fires killed three firefighters, injured 113 civilians, and caused $190 million in damage.

The kitchen was the most common place the fires started, accounting for 54 percent of the blazes.

Some type of cooking equipment was involved in 48 percent of the fires and 49 percent of the injuries. Chimneys or vents were responsible for 3 percent of the fires; grease hood and duct exhaust fans for 1 percent.

When it comes to weak regulations for grease-cleaning companies, Massachusetts is not alone. No states and only a few municipalities, including Corpus Christi, Texas, have instituted training and certification requirements since 1998, when the national codes were revised to include the training language for grease-inspection and cleaning companies.

Industry specialists say that if more state and local governments instituted training standards, more fires could be prevented and lives saved.

"The code was primarily created because the industry needed some standard," said Robert M. Hinderliter, chairman of the training committee for the International Kitchen Exhaust Cleaning Association, which is pushing for higher industrywide standards.

"If they look at them and pay attention to them, it will make a major difference" in preventing fires.
 
g258258dc4a15f851cbaa8aa3ba168c8fda688a64413849.jpg
 
Not to take any heat off the service company, but it amazes me that the city officials and inspectors show very little concern that the inspections were past due and a proper inspection could have avoided this catastrophe. Until there is accountabilty for inspectors, as well as bad cleaners, nothing will change. The inspectors must be held responsible for allowing a kitchen to operate with fire hazzards and safety hazzards present, if they do their job the inadequate service companies will either start doing it right, or get out of KEC. The restaurant owner, city government, and KEC company, should all be held accountable for neglegence, and be charged with maximum penalty.
 
Why am I not Suprised it was an asian restaurant.. I am a business owner.. This is a bad deal.. I clean it all to bare metal or I dont Clean it... I have talked with Asian Restaurants before in the past , they have wanted me to clean the vent hood every 6 months ,, my answer is NO WAY... These restaurants need to be cleaned alot more frequent , more lke once a month..I think thats where the picture taking comes into play.. When I take dated photos of my cleanings I can protect myself... Also whoever heard of such nonsense as to clean the fan and the hood and not clean the duct work.. I know companies do it , and I know companies have probably been asked to clean half the system.. But hey the answer should have been NO ( and the Quote should have been " The ENTIRE systen shall be cleaned to bare metal when any grease laden vapors are found to be present... ((THATS IT IN A NUTSHELL))
 
Most Chinese restaurants here need cleaning at least every 2 to 3 months...

8-3.1 Hoods, grease removal devices, fans, ducts, and other appurtenances shall be cleaned to bare metal at frequent intervals prior to surfaces becoming heavily contaminated with grease or oily sludge. After the exhaust system is cleaned to bare metal, it shall not be coated with powder or any other substance. The entire exhaust system shall be inspected by a properly trained, qualified and certified company or person(s) acceptable to the authority having jurisdiction in accordance with Table 8-3.1.

Type or Volume of Cooking
Frequency

Systems serving solid fuel cooking operations
Monthly

Systems serving high-volume cooking operations such as 24-hour cooking, charbroiling or wok cooking


Quarterly

Systems serving moderate-volume cooking operations
Semi-Annually

Systems serving low-volume cooking operations, such as churches, day camps, seasonal businesses, or senior centers


Annually


Quote from NFPA 96...

Chinese restaraunts use solid fuel cooking which is monthly cleaning and they use woks every 3 month cleaning... So I say every month to 3 months depending on there location and amount of business...
 
When I take dated photos of my cleanings I can protect myself... Also whoever heard of such nonsense as to clean the fan and the hood and not clean the duct work.. I know companies do it , and I know companies have probably been asked to clean half the system.. But hey the answer should have been NO

Hoods are clean regularly, like every couple days? YES?????????

Isnt the hood the safety between the fluuuuuuuuuuuu?
 
When Grease laden vapors are found to be evident.. the entire system shall be cleaned to bare metal..

Hoods, grease removal devices, fans, ducts, and other appurtenances shall be cleaned to bare metal at frequent intervals prior to surfaces becoming heavily contaminated with grease or oily sludge. After the exhaust system is cleaned to bare metal, it shall not be coated with powder or any other substance. The entire
 
So are we saying he took to long between service?

I'm saying the service company was not capable of handling the work load. Instead of learning how to do their job correctly, they caused a fire that killed two firemen.
 
I'm saying the service company was not capable of handling the work load. Instead of learning how to do their job correctly, they caused a fire that killed two firemen


that's a big assumption.
 
So what do we say when a restaurant owner ask us to clean the hood and the fan but not the duct... I have really never heard of this before but I guess if the owner only specified the hood and fan and not the duct it shoul have never been cleaned by a proffesinal cleaning company tha follows the NFPA CODE as staed above.. However since this was clearly not the case and as most judges are probably not to up to date on fire codes I would say they would hold the owner as well as the cleaning company liable.. Now if the NFPA and the fire codes are questioned in a court then neglegence on the cleaning companies part would play a big part for not following the NFPA 96 Code.. Sad part about this ( TO ME ) is why a company that is cleaning vent hoods would even consider a job where they would not clean the entire system as stated.. I think Josh said it right , not so much as a work load but the simple fact that these cleaners did not have the slightest idea of or about the fire code ... I have had customers offer to buy hood cleaning stickers from me with no cleaning, I have had customers ask me how much just to clean what you can see, I have had oriental reataurants mostly ask me to just clean the filters and then put a tag on it offering anywhere from 50.00 to 100.00 dollars.. I always say no and for them to call someone else... When you don't do it by the BOOK ( NFPA) you are asking for trouble... I feel sorry for the families of these two firefighters because really no matter whose fault it was to lose your life on duty over something that could have easily been avoided by companies and owners following The codes and rules set forth by the NFPA , this just makes it hard for me to understand how this certian cleaning and inspection of the cleaning got so far out of hand.. There are going to be alot of people held liable in this one it looks like...
 